Здравствуйте!
ПЛК перестал видеться через Debug port. Т.е., Кодесис его не видит (через Ethernet работает). Плюс не работает кнопка Старт/Стоп. Перепрошил версией 2.03 - не может записать local_addres.dat. Записал руками. Проект грузится только через Ethernet. Контакты проверял, кабель прозванивал, лог загрузки прилагаю.
Код:DATAFLASH initialized successful Welcome to the OWEN program loader MAIN_OSCILLATOR_CLOCK=15998976 PCK=199987200 MCK=66662400 Kernel found... Loading kernel... Reseting... Checksum OK! Load PLC core... Main oscilator clock=15998976 Processor clock=199987200 Master clock=66662400 Waiting for check power... Power status OK Initialization of Power control completed at 20080004, s=16 Initialization of Timer0 completed Module Id=1 found Module Id=2 found Module Id=3 found Module Id=100 found Module Id=101 found Module Id=102 found Module Id=103 found Module Id=104 found Module Id=106 found Module Id=107 found Module Id=120 found Module Id=200 found Module Id=2000 found Module Id=2050 found Module Id=2051 found Module Id=2052 found Module Id=2053 found Module Id=2054 found Module Id=2055 found Module Id=2056 found Module Id=2057 found Module Id=2058 found Module Id=2059 found Module Id=2060 found Module Id=2061 found Module Id=2062 found Module Id=2063 found Module Id=2064 found Module Id=2065 found Module Id=201 found Module Id=202 found Module Id=2100 found Module Id=250 found Module Id=302 found Module Id=303 found Module Id=450 found Module Id=451 found Module Id=452 found Module Id=500 found Module Id=502 found Module Id=504 found Module Id=550 found Module Id=600 found Module Id=601 found Module Id=602 found Module Id=650 found Module Id=700 found Module Id=701 found Module Id=702 found Module Id=703 found Module Id=704 found Module Id=221 found Module Id=300 found Module Id=561 found Module Id=400 found Module Id=402 found Module Id=401 found Initialization of Timer5 completed Begin search and initialize I2C devices Check for adress 72 ...DEVICE FOUND! MCP9800 #0 OK! Check for adress 77 ...DEVICE FOUND! MCP9800 #1 OK! Check for adress 4 ...DEVICE FOUND! PIC lower initialized! Check for adress 3 ...DEVICE FOUND! PIC upper initialized! at 2008003c, s=4 at 20080044, s=4 at 2008004c, s=4 at 20080054, s=4 at 2008005c, s=4 at 20080064, s=4 DATAFLASH READ OK Flash read takes 3317 ms Start mounting FFS Flash check takes 1594 ms Mounting of FFS completed! Mounting takes 83 ms Total size of filesystem is 3145728 bytes It is 6142 blocks It is 2 used blocks It is 0 bad blocks Maximum wear level is 3 times Reset status information....................... PLC was reset by power! Last run module Id =-1 Last post module Id =-1 Total control code =18 Max cache utilisation =3 local_status =1 run_level =2 Run levels stack: ff 16 ff ff ff 0 0 0 0 0 0 0 0 0 0 0 ................................................ Initialization of Timer4 completed ADC and DAC driver initialized! PLC model MODEL PLC 154 Binary VERSION 2.03.0 Need Target version 2.02 Compiled: 11:31:14 Dec 26 2007 MAC 0A:06:0A:0A:0A:0A IP 10.0.6.10 GATE 10.0.6.1 MASK 255.255.255.0 Licence unlimited Current DAC PIC version is 09 Loading PLC core completed! Start CoDeSys initialization secuence Initialization of USB device CDC completed LZS initialization susesful Try to open boot project...**** ERROR: Can not open Checksum file ****