Тема: ПЛК 100 отвалился

  1. #1

    По умолчанию ПЛК 100 отвалился

    ПЛК 100 перестал подключаться по ethernet и RS-232. При сбросе гипертерминал выдает следующее:
    DATAFLASH initialized successful

    Welcome to the OWEN program loader 1.3
    Kernel found...
    Loading kernel...
    Reseting...
    Checksum OK!
    local_status =bLoad PLC core...
    Main oscilator clock=15998976
    Processor clock=179988480
    Master clock=59996160
    Waiting for check power...
    Power status OK
    at 20080004, s=16
    Initialization of Timer0 completed
    Module Id=1 found
    Module Id=2 found
    Module Id=3 found
    Module Id=100 found
    Module Id=101 found
    Module Id=102 found
    Module Id=110 found
    Module Id=103 found
    Module Id=104 found
    Module Id=200 found
    Module Id=2000 found
    Module Id=2050 found
    Module Id=2051 found
    Module Id=2052 found
    Module Id=2053 found
    Module Id=2054 found
    Module Id=2055 found
    Module Id=2056 found
    Module Id=2057 found
    Module Id=2058 found
    Module Id=2059 found
    Module Id=2060 found
    Module Id=2061 found
    Module Id=2062 found
    Module Id=2063 found
    Module Id=2064 found
    Module Id=2065 found
    Module Id=201 found
    Module Id=202 found
    Module Id=210 found
    Module Id=2100 found
    Module Id=211 found
    Module Id=250 found
    Module Id=302 found
    Module Id=303 found
    Module Id=450 found
    Module Id=451 found
    Module Id=452 found
    Module Id=500 found
    Module Id=502 found
    Module Id=504 found
    Module Id=550 found
    Module Id=600 found
    Module Id=601 found
    Module Id=602 found
    Module Id=650 found
    Module Id=221 found
    Module Id=300 found
    Module Id=560 found
    Module Id=561 found
    Module Id=400 found
    Module Id=402 found
    Module Id=401 found
    Initialization of Timer5 completed
    Initialization of Timer4 completed
    USB type code=0
    Version 2 detected
    Test Complited USB slot is present in PLC!!!
    Host is not connected
    Start init USB driver !!!
    Start init USB - Serial number OK.
    Initialization of USB device CDC completed
    Begin search and initialize I2C devices
    Check for adress 77 ...DEVICE FOUND!
    MCP9800 #0 OK!
    Check for adress 72 ...FAILED!
    Check for adress 4 ...DEVICE FOUND!
    PIC lower initialized!
    Check for adress 3 ...DEVICE FOUND!
    PIC upper initialized!
    at 2008003c, s=4
    at 20080044, s=4
    Read Flash: .at 2008004c, s=4
    at 20080054, s=4
    ..................at 2008005c, s=4
    .................................................. .............................. ..
    DATAFLASH READ OK

    Flash read takes 3490 ms
    Start mounting FFS
    Flash check takes 2326 ms
    It is 0 bad blocks
    Mounting of FFS completed!
    Mounting takes 180 ms
    Total size of filesystem is 3145728 bytes
    It is 6015 blocks
    It is 129 used blocks
    It is 0 bad blocks
    Maximum wear level is 85 times

    Reset status information.......................
    PLC was reset by power!

    Last run module Id =-1
    Last post module Id =-1
    Total control code =18
    Max cache utilisation =2
    local_status =b
    run_level =1
    Run levels stack: ff ff ff ff ff 0 0 0 0 0 0 0 0 0 0 0
    ................................................
    Slave Retain loaded
    at 200800ac, s=28
    PLC model MODEL PLC 100
    Binary VERSION 2.14.0
    Need Target version 2.10
    Compiled: 10:44:59 May 16 2011
    MAC 6A:77:00:00:65:7E
    IP 10.0.6.11
    GATE 10.0.6.1
    MASK 255.255.255.0
    PIC upper version is 07
    Licence unlimited
    No DAC
    PIC lower version is 0a

    Loading PLC core completed!

    Start CoDeSys initialization secuence
    Initialization of USB device CDC completed
    LZS initialization susesful
    Try to open boot project...
    **** ERROR: Can not open Checksum file ****
    По IP вроде пингуется:
    ping 10.0.6.11

    Обмен пакетами с 10.0.6.11 по с 32 байтами данных:
    Ответ от 10.0.6.11: число байт=32 время<1мс TTL=128
    Ответ от 10.0.6.11: число байт=32 время<1мс TTL=128
    Ответ от 10.0.6.11: число байт=32 время<1мс TTL=128
    Ответ от 10.0.6.11: число байт=32 время<1мс TTL=128

    Статистика Ping для 10.0.6.11:
    Пакетов: отправлено = 4, получено = 4, потеряно = 0
    (0% потерь)
    Приблизительное время приема-передачи в мс:
    Минимальное = 0мсек, Максимальное = 0 мсек, Среднее = 0 мсек
    Обратил внимание на
    Check for adress 72 ...FAILED!
    Собственно вопросы - что это такое и как лечить? Предполагаю, что перепрошивкой, но инструкцию по перепрошивке найти не смог.
    Последний раз редактировалось Кулаков Андрей; 15.02.2013 в 06:17.

  2. #2

  3. #3

    По умолчанию

    Перепрошейте контроллер.
    То, что 72 Failed для ПЛК100 нормально (этот элемент только в ПЛК150 запаивается )

  4. #4

    По умолчанию

    Контроллер не шьется. Программа прошивки не находит ip и mac адрес. Codesys по rs-232 подключается строго через день - позавчера не хотел, вчера весь день через него коннектил, сегодня опять не хочет. Чувствую себя Алисой в стране чудес.