Например так:
При опросе bool регистров контроллера с адресом 246 ответ полноценный, например:
Packet: MODBUS Request (packet size: 8, data size: 4), 2025‐05‐22 16:25:37.602401 +0.000000
Mode: RTU Mode
Address: 246 (Slave)
Function: 2 (Read Discrete Inputs)
Starting Address: 4724
Quantity: 2
CRC: 61097 (OK)
Packet: MODBUS Response (packet size: 6, data size: 2), 2025‐05‐22 16:25:37.714816 +0.000000
Mode: RTU Mode
Address: 246 (Slave)
Function: 2 (Read Discrete Inputs)
Starting Address: 4724
Quantity: 8
Values: Input0: 0 Input1: 0 Input2: 0 Input3: 0 Input4: 0 Input5: 0 Input6: 0 Input7: 0
CRC: 64659 (OK)
При опросе bool регистров (по контуру ГВС) контроллера с адресом 247 ответ полноценный, например:
Packet: MODBUS Request (packet size: 8, data size: 4), 2025‐05‐22 16:33:21.138886 +0.000000
Mode: RTU Mode
Address: 247 (Slave)
Function: 2 (Read Discrete Inputs)
Starting Address: 4325
Quantity: 2
CRC: 27384 (OK)
Packet: MODBUS Response (packet size: 6, data size: 2), 2025‐05‐22 16:33:21.342707 +0.000000
Mode: RTU Mode
Address: 247 (Slave)
Function: 2 (Read Discrete Inputs)
Starting Address: 4325
Quantity: 8
Values: Input0: 1 Input1: 0 Input2: 0 Input3: 0 Input4: 0 Input5: 0 Input6: 0 Input7: 0
CRC: 49235 (OK)
А вот при опросе bool регистров (по контуру вентиляции) того же контроллера с адресом 247 ответ меньше на 1 байт (байт с данными), например:
Packet: MODBUS Request (packet size: 8, data size: 4), 2025‐05‐22 16:39:39.603747 +0.000000
Mode: RTU Mode
Address: 247 (Slave)
Function: 2 (Read Discrete Inputs)
Starting Address: 4911
Quantity: 1
CRC: 4504 (OK)
Packet: MODBUS Response (packet size: 5, data size: 1), 2025‐05‐22 16:39:39.780263 +0.000000
Mode: RTU Mode
Address: 247 (Slave)
Function: 2 (Read Discrete Inputs)
CRC: 37376 (OK)