Просмотр полной версии : Factory default for ПЛК 150?
k2teknik
18.02.2015, 13:28
Is there a way to set Factory default on ПЛК 150?
I may have put wrong IP info into my ПЛК 150, so now no contact via Ethernet interface.
The RS232 interface will not work so I am searching a way to reset all setting inside ПЛК 150 included TCP/IP settings.
Regards
The factory settings will not dump TCP/IP settings. If you can connect to ПЛК 150 over rs232 then take a look plc browser (codesys) file local_addres.dat. it is your IP (in HEX).
k2teknik
06.03.2015, 13:54
The factory settings will not dump TCP/IP settings.Ok, so that is no option.
If you can connect to ПЛК 150 over rs232 then take a look plc browser (codesys) file local_addres.dat. it is your IP (in HEX).I got a new USB-RS232 converter and can connect via RS232.
But would still like a way to reset to factory settings (as much as possibly), right now I have one PLC running in an endless reboot loop and see no way to stop him. I had tried holding RESET+pressing START for 10 seconds but way to clear the present code in memory.